>The Overview page in the webinterface shows there is power in the
>UPS form over 2 hours. How can I force a faster automatic freebsd
>shutdown to see if it is working (can't wait 2 hours)
Try setting the battery level in apcupsd.conf to a high value like 90%
# If during a power failure, the remaining battery percentage
# (as reported by the UPS) is below or equal to BATTERYLEVEL,
# apcupsd will initiate a system shutdown.
BATTERYLEVEL 90
#
You need to restart the apc daemon after you adjust the config files.
Doing
apcaccess
from the shell, should reflect your changes.
>
>
>but do these refer to shutdown of a unix client or shutdown of the UPS
>itself?
On the apc units I have used, it will send the "shutdown" signal to
the UPS, so it will cut power to all the ports until street power
comes back.
---Mike